Author |
Message |
Gerald_D
Registered Username: Gerald_d
Post Number: 112 Registered: 11-2005
| Posted on Saturday, June 03, 2006 - 08:55 pm: |
|
This was the project for today..... Basically the power supply, parallel connector board and 4 geckos...... (A stepper motor is included in the pic to get a sense of scale) .....needed a home. So we get a metal box.... Also, we need a thermistor relay and 9V transformer for the parallel board.... ....and a main switch, a couple of terminals and a circulating fan. The white plate in the back of the box is taken out for the assembly. The idea is to lift the geckos about 60mm off the back plane and mount them on an alu plate which acts as a heat sink and ground/earth plane..... ......The rail in front is a standard 35mm DIN rail. (Also lifted off the back-plane in case wires/cables need to pass under it. The fan sucks air from behind the white back plane (which is spaced 15 mm off the back of the box) and blows against the bottom of the alu plate.... More wiring and tidying up to do, and then it can all be dropped back into the "orange" box. |
Gerald_D
Registered Username: Gerald_d
Post Number: 122 Registered: 11-2005
| Posted on Sunday, June 11, 2006 - 06:16 pm: |
|
Some more progress this weekend - wiring is about 95% done....... The last pic is a view looking into the terminals that will receive the cables leading out of the control box. 1. The main power cable, with 3x Line and 1x Neutral conductors feed into the isolator switch with the blue knob on top. The 1x Ground conductor of the infeed cable goes to a point bottom right, on the mounting screw of the white back plate. 2. The outfeed to the VFD for the spindle, 3x Line comes from the contactor to the right of the isolator. 3. The empty terminals further right are for the shielded cables to the E-stops, Z-zero, etc. All Inputs. The shields also have terminals dedicated to them. 4. Nearly everything to the left of the blue-topped isolator is for the spindle. The first five terminals are for the thermistor and cooling fan. (Plus a shield terminal) 5. Then the tall thermistor relay. 6. Next few terminals are the outputs from the PMDX board - some are not allocated yet. 7. The last terminals to the left are for the communications with the VFD. Start/stop of the spindle, Fault at the VFD, Analog speed control via potentiometer. 8. Lastly, each stepper motor (shielded) cable goes directly into its Gecko via the blue terminals at the top of the pic. The shield of the cable screws to the alu plate. |
Gerald_D
Registered Username: Gerald_d
Post Number: 123 Registered: 11-2005
| Posted on Monday, June 12, 2006 - 07:00 am: |
|
A wiring project like this is a good "kitchen table" project. This is all being done at home, and it is actually fairly relaxing. (Do you still want a simplified schematic of motors/geckos etc.?) |
Gerald_D
Registered Username: Gerald_d
Post Number: 127 Registered: 11-2005
| Posted on Saturday, June 17, 2006 - 04:03 pm: |
|
That orange box got a few holes it, and was sprayed "MechMate Blue" (actually it is standard aerosol "Electric Blue from the local hardware shop) Then some more wiring...... Until the outside looks nearly finished...
|
Mike Richards
Registered Username: Richards
Post Number: 15 Registered: 05-2006
| Posted on Saturday, June 17, 2006 - 06:16 pm: |
|
Gerald, You've done a beautiful job. I wish that my designs looked so good. If I may make one suggestion, though. You might want to place all switches on a side panel. Even though a door in a control box is rarely opened, meaning that the cables will never be flexed enough to 'crack', there is always the possibility that a cable might get wedged. Of course the ON/OFF switch has to extend through the door so that the door can't be opened while the unit is powered up, but that is usually just the 'handle' of the switch, with the contact portion firmly mounted on the interior of the box (as you have done). |
Gerald_D
Registered Username: Gerald_d
Post Number: 131 Registered: 11-2005
| Posted on Saturday, June 17, 2006 - 06:56 pm: |
|
I considered side switches/lights but discarded that for three reasons: - the box will be wall mounted and the right side is far away from the operator, in a corner. The left side will be obstructed by the VFD. - the indicator lights need to to be visible over a wide angle, from the front - the white back panel cannot be dropped in if switches are on the sides. By the way, to explain the outside features: - the white rectangles are plug outlets for powering the PC and another appliances if necessary. - The yellow/red isolator is obvious. Switching that on gives power to everything except the VFD/Spindle and the linear power supply and Geckos. The actual power switched is very low (PMDX, fan, thermistor relay). - The green pilot comes on when isolator is on. - the rectangular red/green/pilot controls the contactor that powers the VFD and linear power supply. (The E-Stops, thermistor relay, VFD malfunction, drop this contactor out). Pilot is lit when "drives" are powered. - silver/grey knob for spindle speed control. - black button next to it is a detent push-push for starting the spindle for warm-up without starting the PC. - the empty top section of the front is for the logo decal! :-) |
Gerald_D
Registered Username: Gerald_d
Post Number: 152 Registered: 11-2005
| Posted on Sunday, July 02, 2006 - 09:08 pm: |
|
Here is the mounted control box, with the Delta VFD alongside. The "base" of the VFD houses the output line reactor.
|
krymis
Registered Username: Krymis
Post Number: 1 Registered: 08-2006
| Posted on Friday, August 04, 2006 - 04:13 pm: |
|
what size box and where did you get it? |
Gerald_D
Registered Username: Gerald_d
Post Number: 195 Registered: 11-2005
| Posted on Tuesday, August 22, 2006 - 09:48 am: |
|
The box is 550Hx400Wx220D (millimeters) external. Dust proof (door seal), with removable back-plate. Got a no-name brand here in South Africa (part no. HE203 from www.em.co.za), about $150 The COOLING fan system works like a champ! Have been logging internal and external temps over the last 2 months and the max differential was 12 degrees Centigrade. Because the fan does not draw in outside air, there are no dust issues. The box dissipates heat through its surface skin - the larger the box, the better the cooling. |
Mike John
Registered Username: Mikejohn
Post Number: 49 Registered: 12-2005
| Posted on Tuesday, August 22, 2006 - 12:33 pm: |
|
Gerald, Although I realise price comparisons between countries (even continents), are not necessarily indicative, I would still be interested in the complete cost (including cabinet) of your control box. ..........Mike |
Gerald_D
Registered Username: Gerald_d
Post Number: 196 Registered: 11-2005
| Posted on Tuesday, August 22, 2006 - 01:33 pm: |
|
Without the shipping costs to get the Gecko's and PMDX here, it cost $970 in materials & components alone. (no labour) |
Deon Gerber
Registered Username: Deon
Post Number: 1 Registered: 10-2006
| Posted on Monday, October 23, 2006 - 08:30 pm: |
|
Hi Gerald I am a newby when you talk about electronics.Can you give me more info on the output line reactor that is in the base of the vfd mount. What is its purpose. Nice forum you built up.... Thanks Deon |
Gerald_D
Registered Username: Gerald_d
Post Number: 324 Registered: 11-2005
| Posted on Monday, October 23, 2006 - 08:49 pm: |
|
Hallo Deon daar in PE! The output line reactor (some people call it a choke) is highly recommended by both the VFD and spindle manufacturers. I didn't want to argue with them. Here is the one that I am using. The stuff on that page explains some of the benefits: Protect motors from long lead effects Reduce output voltage dv/dt Virtually eliminate nuisance tripping Extend semiconductor life Reduce harmonic distortion Reduce surge currents Reduce motor temperature Reduce motor audible noise Improve true power factor etc. Anyway, I had heard that VFD's make radios go funny, but so far we havn't had a single issue caused by the VFD in the shop. Maybe it is because we used a "reactor"? Another reference |
Gerald_D
Registered Username: Gerald_d
Post Number: 407 Registered: 11-2005
| Posted on Thursday, November 09, 2006 - 07:56 am: |
|
Spoke too soon - have just discovered that the VFD is inducing a fake charge pump signal to the MechMate's own controller if the PC is not supplying the real charge pump signal. see this thread. This doesn't make a reactor a bad choice though, I still think it is the very first accessory to consider for a VFD/spindle setup. |
Gerald_D
Registered Username: Gerald_d
Post Number: 812 Registered: 11-2005
| Posted on Monday, February 05, 2007 - 09:27 pm: |
|
People are asking what the following components do.....? From the left: 1: Thermistor relay. Only used to protect a spindle against overheating....if the spindle has an internal thermistor. If you are using a router, you don't need it. If your spindle does not have a thermistor, you don't need it. (See other picture in first post of this thread) (Siemens 3RN) 2. Main switch: Operated by the red/yellow knob on the outside of the door. You can only open the door if the switch is OFF. It has 4 poles to break the 3 phases Live and the Neutral lines. You can put your safety switches somewhere else if you want. This is the "export" quality way of doing it. (Ensto - Finland. brochure) 3. Main Relay/Contactor: Needed for the emergency stop circuit so that it can switch OFF all the high voltage when an Emergency Stop button is pushed. Again, this is "export" quality safety - you can decide on your own safety standard. (local source) 4. 9 Volt transformer: to supply the PMDX-122 with power. You can also supply 5V from your PC's USB port, but my PC is old and does not have USB ports. (See other picture in first post of this thread) I mounted the transformer on the green base.
|
Hugo Carradini
Registered Username: Hugotel
Post Number: 10 Registered: 11-2006
| Posted on Tuesday, February 06, 2007 - 02:28 am: |
|
I was wondering but was timid to ask . It looks like a nice configuration. |
Gerald_D
Registered Username: Gerald_d
Post Number: 813 Registered: 11-2005
| Posted on Tuesday, February 06, 2007 - 03:08 am: |
|
Hi Hugo I am sorry for my bad reputation which makes you timid Maybe I must explain why some people get "unpleasant" answers from me at times..... There seem to be two types of people who want to build MechMates - a. Those that like the looks and are too lazy to think and b. Those that want to understand why and what they need to do. I believe that group a. is dangerous and end with the risk of electrocuting themselves - I do not plan to help these guys make accidents. It is easy to identify this group - the first thing they want is a shopping list to start buying stuff! Hugo, you are clearly in the second group - you are trying to find out the purpose of each item before you decide to buy it. Just think of the implication if I put that Ensto switch on a shopping list..... They are a company from Finland who happen to have a stockist in South Africa. In your country there could be another more economical supplier - remember, it is only a switch. Also, if you are going to use a router, you could use single phase only, so the switch, (and the contactor) can be much smaller. The title of this thread has always carried the words screened, spindle, 3-phase, "export". People need to realise that their own application could be different and build their control boxes accordingly. |
Hugo Carradini
Registered Username: Hugotel
Post Number: 33 Registered: 11-2006
| Posted on Saturday, February 17, 2007 - 11:01 pm: |
|
Thanks Gerald. You can count with a MechMate "beast" done the right way in my country ¿How do you install the 9 volt transformer? It has five legs. ¿How you configured them? ¿Size or capacity of the Main Relay/Contactor? To many questions, but I am making my list for buying all ,and this is my weak area. Thanks |
Gerald_D
Registered Username: Gerald_d
Post Number: 921 Registered: 11-2005
| Posted on Sunday, February 18, 2007 - 07:10 am: |
|
Those five legs on that transformer confused me as well - I had to phone the supplier to find the diagram. Your transformer will be different and it is important only to buy stuff for which you can get information. This mostly means that you cannot buy from the cheapest supplier. For the "main contactor" capacity you need to decide a lot of things. Spindle or router (and size), how your "safety" standards and plan will work, voltage in your country, etc. |
Mike Richards
Registered Username: Richards
Post Number: 47 Registered: 05-2006
| Posted on Sunday, February 18, 2007 - 03:01 pm: |
|
Usually five legs on a transformer means that you have two legs for the primary (input) voltage and three legs for the secondary (output) voltage. The output voltage would have a center tap so that a 9V transformer would produce 4.5V (times 2) or 9V, |
Loren Gameros
Registered Username: Moron_wizard
Post Number: 2 Registered: 02-2007
| Posted on Sunday, February 18, 2007 - 11:22 pm: |
|
Hi Gerald, Do you have a wiring diagram that would show all connections lets say for example the power supply? Thank You. |
Gerald_D
Registered Username: Gerald_d
Post Number: 933 Registered: 11-2005
| Posted on Monday, February 19, 2007 - 07:37 am: |
|
I am very nervous about requests for power supply wiring diagrams. I believe that people who understand the risks of working with mains voltages will not need such diagrams. |
Loren Gameros
Registered Username: Moron_wizard
Post Number: 3 Registered: 02-2007
| Posted on Monday, February 19, 2007 - 10:08 am: |
|
Ok,understandable. Maybe I'll re-word that question. What I am looking for is something like this. |
Gerald_D
Registered Username: Gerald_d
Post Number: 935 Registered: 11-2005
| Posted on Monday, February 19, 2007 - 10:58 am: |
|
You can use that same diagram for a MechMate. On the right side, the PARALLEL PORT PINS are all on the PMDX-122 card. On the left side, the AC PLUG and SPINDLE PLUG is confusing for me. Not sure which is a PLUG or socket, which is the power cord that goes to the wall socket/outlet..... I think that: - AC PLUG is the incoming power cord - SPINDLE PLUG is a socket for plugging a single phase router into. (We normally use the term SPINDLE for another type of cutting motor) - RELAY is standard. We often call it a CONTACTOR, and we often try to break both Live(Hot) and Neutral with 2 poles on that contactor. But if your government/personal laws/standards allow a single pole relay then that is okay. - S1 & S2 are E-stops contacts or just plain Stop/Start contacts. Not clear how these switches are used. This circuit will not stop/start the router on command from Mach3. Something more is needed. We do not use the bleed resistor R1 at bottom left because the 4 Geckos drain the capacitor (C1) quickly enough when the power is cut. |
Gerald_D
Registered Username: Gerald_d
Post Number: 936 Registered: 11-2005
| Posted on Monday, February 19, 2007 - 11:07 am: |
|
This is the only diagram that I have: If you look closely, you will see that it does not give the power supply schematic in top left corner. Also, it does not give all the Gecko connections. I can give a copy of this schematic to people who have purchased exactly the same components (including spindle and VFD). Subsequent to this exchange, I have ventured into general purpose power/wiring diagrams here |
Edmond Duncan Kevin Enslin
Registered Username: Edmeister
Post Number: 1 Registered: 02-2007
| Posted on Monday, February 26, 2007 - 07:37 am: |
|
Hi Gerald Is there a local source of all the components for the control box, also I only want to run single phase at the moment.What is the total cost of building the controller box. Thanks Edmond |
Gerald_D
Registered Username: Gerald_d
Post Number: 1027 Registered: 11-2005
| Posted on Monday, February 26, 2007 - 08:03 am: |
|
Only stuff not off-the-shelf in Cape Town are the Gecko's, PMDX card, and transformer. Gecko's and transformer ex-JHB. The JHB gecko stockist has an equivalent to the PMDX (www.cncdirect.co.za)(Gecko202 @ $200). Transformer can be ordered via Communica. Most other parts from ElectroMechanica, Bellco and Communica. Total cost depends on where the components come from, whether you import direct and the discounts you can get - my material cost about R6000? (But that could be nearer R9000 with inefficient shopping) ($833 to $1250). Also add sweat & time..... |