This was the project for today.....

Basically the power supply, parallel connector board and 4 geckos......
1
(A stepper motor is included in the pic to get a sense of scale)

.....needed a home.

So we get a metal box....
2aa 2a


Also, we need a thermistor relay and 9V transformer for the parallel board....
3aa 3a

....and a main switch, a couple of terminals and a circulating fan.

The white plate in the back of the box is taken out for the assembly. The idea is to lift the geckos about 60mm off the back plane and mount them on an alu plate which acts as a heat sink and ground/earth plane.....
4aa 4a

......The rail in front is a standard 35mm DIN rail. (Also lifted off the back-plane in case wires/cables need to pass under it.

The fan sucks air from behind the white back plane (which is spaced 15 mm off the back of the box) and blows against the bottom of the alu plate....
5aa 5a


More wiring and tidying up to do, and then it can all be dropped back into the "orange" box.
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 122
Registered: 11-2005
Posted on Sunday, June 11, 2006 - 06:16 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Some more progress this weekend - wiring is about 95% done.......

1
2
3
4
5
6


The last pic is a view looking into the terminals that will receive the cables leading out of the control box.

1. The main power cable, with 3x Line and 1x Neutral conductors feed into the isolator switch with the blue knob on top. The 1x Ground conductor of the infeed cable goes to a point bottom right, on the mounting screw of the white back plate.

2. The outfeed to the VFD for the spindle, 3x Line comes from the contactor to the right of the isolator.

3. The empty terminals further right are for the shielded cables to the E-stops, Z-zero, etc. All Inputs. The shields also have terminals dedicated to them.

4. Nearly everything to the left of the blue-topped isolator is for the spindle. The first five terminals are for the thermistor and cooling fan. (Plus a shield terminal)

5. Then the tall thermistor relay.

6. Next few terminals are the outputs from the PMDX board - some are not allocated yet.

7. The last terminals to the left are for the communications with the VFD. Start/stop of the spindle, Fault at the VFD, Analog speed control via potentiometer.

8. Lastly, each stepper motor (shielded) cable goes directly into its Gecko via the blue terminals at the top of the pic. The shield of the cable screws to the alu plate.
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 123
Registered: 11-2005
Posted on Monday, June 12, 2006 - 07:00 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

A wiring project like this is a good "kitchen table" project. This is all being done at home, and it is actually fairly relaxing.

(Do you still want a simplified schematic of motors/geckos etc.?)
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 127
Registered: 11-2005
Posted on Saturday, June 17, 2006 - 04:03 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

That orange box got a few holes it, and was sprayed "MechMate Blue" (actually it is standard aerosol "Electric Blue from the local hardware shop)

holy


Then some more wiring......

2
3


Until the outside looks nearly finished...

4
Top of pagePrevious messageNext messageBottom of page Link to this message

Mike Richards
Registered
Username: Richards

Post Number: 15
Registered: 05-2006
Posted on Saturday, June 17, 2006 - 06:16 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Gerald,
You've done a beautiful job. I wish that my designs looked so good.

If I may make one suggestion, though. You might want to place all switches on a side panel. Even though a door in a control box is rarely opened, meaning that the cables will never be flexed enough to 'crack', there is always the possibility that a cable might get wedged. Of course the ON/OFF switch has to extend through the door so that the door can't be opened while the unit is powered up, but that is usually just the 'handle' of the switch, with the contact portion firmly mounted on the interior of the box (as you have done).
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 131
Registered: 11-2005
Posted on Saturday, June 17, 2006 - 06:56 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

I considered side switches/lights but discarded that for three reasons:

- the box will be wall mounted and the right side is far away from the operator, in a corner. The left side will be obstructed by the VFD.

- the indicator lights need to to be visible over a wide angle, from the front

- the white back panel cannot be dropped in if switches are on the sides.

By the way, to explain the outside features:

- the white rectangles are plug outlets for powering the PC and another appliances if necessary.

- The yellow/red isolator is obvious. Switching that on gives power to everything except the VFD/Spindle and the linear power supply and Geckos. The actual power switched is very low (PMDX, fan, thermistor relay).

- The green pilot comes on when isolator is on.

- the rectangular red/green/pilot controls the contactor that powers the VFD and linear power supply. (The E-Stops, thermistor relay, VFD malfunction, drop this contactor out). Pilot is lit when "drives" are powered.

- silver/grey knob for spindle speed control.

- black button next to it is a detent push-push for starting the spindle for warm-up without starting the PC.

- the empty top section of the front is for the logo decal! :-)
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 152
Registered: 11-2005
Posted on Sunday, July 02, 2006 - 09:08 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Here is the mounted control box, with the Delta VFD alongside. The "base" of the VFD houses the output line reactor.

1
Top of pagePrevious messageNext messageBottom of page Link to this message

krymis
Registered
Username: Krymis

Post Number: 1
Registered: 08-2006
Posted on Friday, August 04, 2006 - 04:13 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

what size box and where did you get it?
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 195
Registered: 11-2005
Posted on Tuesday, August 22, 2006 - 09:48 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

The box is 550Hx400Wx220D (millimeters) external. Dust proof (door seal), with removable back-plate. Got a no-name brand here in South Africa (part no. HE203 from www.em.co.za), about $150

The COOLING fan system works like a champ! Have been logging internal and external temps over the last 2 months and the max differential was 12 degrees Centigrade. Because the fan does not draw in outside air, there are no dust issues. The box dissipates heat through its surface skin - the larger the box, the better the cooling.
Top of pagePrevious messageNext messageBottom of page Link to this message

Mike John
Registered
Username: Mikejohn

Post Number: 49
Registered: 12-2005
Posted on Tuesday, August 22, 2006 - 12:33 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Gerald,
Although I realise price comparisons between countries (even continents), are not necessarily indicative, I would still be interested in the complete cost (including cabinet) of your control box.

..........Mike
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 196
Registered: 11-2005
Posted on Tuesday, August 22, 2006 - 01:33 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Without the shipping costs to get the Gecko's and PMDX here, it cost $970 in materials & components alone. (no labour)
Top of pagePrevious messageNext messageBottom of page Link to this message

Deon Gerber
Registered
Username: Deon

Post Number: 1
Registered: 10-2006
Posted on Monday, October 23, 2006 - 08:30 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Hi Gerald

I am a newby when you talk about electronics.Can you give me more info on the output line reactor that is in the base of the vfd mount. What is its purpose.

Nice forum you built up....

Thanks
Deon
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 324
Registered: 11-2005
Posted on Monday, October 23, 2006 - 08:49 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Hallo Deon daar in PE!

The output line reactor (some people call it a choke) is highly recommended by both the VFD and spindle manufacturers. I didn't want to argue with them. :-) Here is the one that I am using. The stuff on that page explains some of the benefits:

Protect motors from long lead effects
Reduce output voltage dv/dt
Virtually eliminate nuisance tripping
Extend semiconductor life
Reduce harmonic distortion
Reduce surge currents
Reduce motor temperature
Reduce motor audible noise
Improve true power factor
etc.

Anyway, I had heard that VFD's make radios go funny, but so far we havn't had a single issue caused by the VFD in the shop. Maybe it is because we used a "reactor"?

Another reference
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 407
Registered: 11-2005
Posted on Thursday, November 09, 2006 - 07:56 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Spoke too soon - have just discovered that the VFD is inducing a fake charge pump signal to the MechMate's own controller if the PC is not supplying the real charge pump signal. see this thread. This doesn't make a reactor a bad choice though, I still think it is the very first accessory to consider for a VFD/spindle setup.
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 812
Registered: 11-2005
Posted on Monday, February 05, 2007 - 09:27 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

People are asking what the following components do.....?

1


From the left:

1: Thermistor relay. Only used to protect a spindle against overheating....if the spindle has an internal thermistor. If you are using a router, you don't need it. If your spindle does not have a thermistor, you don't need it. (See other picture in first post of this thread) (Siemens 3RN)

2. Main switch: Operated by the red/yellow knob on the outside of the door. You can only open the door if the switch is OFF. It has 4 poles to break the 3 phases Live and the Neutral lines. You can put your safety switches somewhere else if you want. This is the "export" quality way of doing it. (Ensto - Finland. brochure)

3. Main Relay/Contactor: Needed for the emergency stop circuit so that it can switch OFF all the high voltage when an Emergency Stop button is pushed. Again, this is "export" quality safety - you can decide on your own safety standard. (local source)

4. 9 Volt transformer: to supply the PMDX-122 with power. You can also supply 5V from your PC's USB port, but my PC is old and does not have USB ports. (See other picture in first post of this thread) I mounted the transformer on the green base.
Top of pagePrevious messageNext messageBottom of page Link to this message

Hugo Carradini
Registered
Username: Hugotel

Post Number: 10
Registered: 11-2006
Posted on Tuesday, February 06, 2007 - 02:28 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

I was wondering but was timid to ask .
It looks like a nice configuration.
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 813
Registered: 11-2005
Posted on Tuesday, February 06, 2007 - 03:08 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Hi Hugo

I am sorry for my bad reputation which makes you timid :-)

Maybe I must explain why some people get "unpleasant" answers from me at times..... There seem to be two types of people who want to build MechMates - a. Those that like the looks and are too lazy to think and b. Those that want to understand why and what they need to do. I believe that group a. is dangerous and end with the risk of electrocuting themselves - I do not plan to help these guys make accidents. It is easy to identify this group - the first thing they want is a shopping list to start buying stuff! Hugo, you are clearly in the second group - you are trying to find out the purpose of each item before you decide to buy it.

Just think of the implication if I put that Ensto switch on a shopping list..... They are a company from Finland who happen to have a stockist in South Africa. In your country there could be another more economical supplier - remember, it is only a switch. Also, if you are going to use a router, you could use single phase only, so the switch, (and the contactor) can be much smaller.

The title of this thread has always carried the words screened, spindle, 3-phase, "export". People need to realise that their own application could be different and build their control boxes accordingly.
Top of pagePrevious messageNext messageBottom of page Link to this message

Hugo Carradini
Registered
Username: Hugotel

Post Number: 33
Registered: 11-2006
Posted on Saturday, February 17, 2007 - 11:01 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Thanks Gerald.

You can count with a MechMate "beast" done the right way in my country

¿How do you install the 9 volt transformer? It has five legs. ¿How you configured them?

¿Size or capacity of the Main Relay/Contactor? To many questions, but I am making my list for buying all ,and this is my weak area. Thanks
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 921
Registered: 11-2005
Posted on Sunday, February 18, 2007 - 07:10 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Those five legs on that transformer confused me as well - I had to phone the supplier to find the diagram. Your transformer will be different and it is important only to buy stuff for which you can get information. This mostly means that you cannot buy from the cheapest supplier.

For the "main contactor" capacity you need to decide a lot of things. Spindle or router (and size), how your "safety" standards and plan will work, voltage in your country, etc.
Top of pagePrevious messageNext messageBottom of page Link to this message

Mike Richards
Registered
Username: Richards

Post Number: 47
Registered: 05-2006
Posted on Sunday, February 18, 2007 - 03:01 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Usually five legs on a transformer means that you have two legs for the primary (input) voltage and three legs for the secondary (output) voltage. The output voltage would have a center tap so that a 9V transformer would produce 4.5V (times 2) or 9V,
Top of pagePrevious messageNext messageBottom of page Link to this message

Loren Gameros
Registered
Username: Moron_wizard

Post Number: 2
Registered: 02-2007
Posted on Sunday, February 18, 2007 - 11:22 pm:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Hi Gerald,

Do you have a wiring diagram that would show all connections lets say for example the power supply? Thank You.
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 933
Registered: 11-2005
Posted on Monday, February 19, 2007 - 07:37 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

I am very nervous about requests for power supply wiring diagrams. I believe that people who understand the risks of working with mains voltages will not need such diagrams.
Top of pagePrevious messageNext messageBottom of page Link to this message

Loren Gameros
Registered
Username: Moron_wizard

Post Number: 3
Registered: 02-2007
Posted on Monday, February 19, 2007 - 10:08 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Ok,understandable. Maybe I'll re-word that question. What I am looking for is something like this.

sample wiring diagram
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 935
Registered: 11-2005
Posted on Monday, February 19, 2007 - 10:58 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

You can use that same diagram for a MechMate.

On the right side, the PARALLEL PORT PINS are all on the PMDX-122 card.

On the left side, the AC PLUG and SPINDLE PLUG is confusing for me. Not sure which is a PLUG or socket, which is the power cord that goes to the wall socket/outlet..... I think that:
- AC PLUG is the incoming power cord
- SPINDLE PLUG is a socket for plugging a single phase router into. (We normally use the term SPINDLE for another type of cutting motor)
- RELAY is standard. We often call it a CONTACTOR, and we often try to break both Live(Hot) and Neutral with 2 poles on that contactor. But if your government/personal laws/standards allow a single pole relay then that is okay.
- S1 & S2 are E-stops contacts or just plain Stop/Start contacts. Not clear how these switches are used.

This circuit will not stop/start the router on command from Mach3. Something more is needed.

We do not use the bleed resistor R1 at bottom left because the 4 Geckos drain the capacitor (C1) quickly enough when the power is cut.
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 936
Registered: 11-2005
Posted on Monday, February 19, 2007 - 11:07 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

This is the only diagram that I have:

1


If you look closely, you will see that it does not give the power supply schematic in top left corner. Also, it does not give all the Gecko connections.

I can give a copy of this schematic to people who have purchased exactly the same components (including spindle and VFD).

Subsequent to this exchange, I have ventured into general purpose power/wiring diagrams here
Top of pagePrevious messageNext messageBottom of page Link to this message

Edmond Duncan Kevin Enslin
Registered
Username: Edmeister

Post Number: 1
Registered: 02-2007
Posted on Monday, February 26, 2007 - 07:37 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Hi Gerald

Is there a local source of all the components for the control box, also I only want to run single phase at the moment.What is the total cost of building the controller box.

Thanks Edmond
Top of pagePrevious messageNext messageBottom of page Link to this message

Gerald_D
Registered
Username: Gerald_d

Post Number: 1027
Registered: 11-2005
Posted on Monday, February 26, 2007 - 08:03 am:   Edit Post Delete Post Print Post    Move Post (Moderator/Admin Only)

Only stuff not off-the-shelf in Cape Town are the Gecko's, PMDX card, and transformer. Gecko's and transformer ex-JHB. The JHB gecko stockist has an equivalent to the PMDX (www.cncdirect.co.za)(Gecko202 @ $200). Transformer can be ordered via Communica. Most other parts from ElectroMechanica, Bellco and Communica. Total cost depends on where the components come from, whether you import direct and the discounts you can get - my material cost about R6000? (But that could be nearer R9000 with inefficient shopping) ($833 to $1250). Also add sweat & time.....

Add Your Message Here
Post:
Username: Posting Information:
This is a private posting area. Only registered users and moderators may post messages here.
Password:
Options: Enable HTML code in message
Automatically activate URLs in message
Action:

Topics | Last Day | Last Week | Tree View | Search | Help/Instructions | Program Credits Administration